Is measuring total panel current required?

Emporia Energy Community Support Center Hardware and Installation Is measuring total panel current required?

Viewing 1 reply thread
  • Author
    Posts
    • #11037 Report Abuse
      emporilio
      Member

      I have a gen 3 Vue. My load center has bus bars; my understanding is that the flexible CTs are not yet available. If they have giant dangling black boxes, it will be a no-go; the load center is extremely crowded and, as much as I’d love to, I can’t replace it with a bigger box.

      So my question is – can I use the Vue without the mains CTs?

    • #11089 Report Abuse
      Kevin @ Emporia
      Emporia Staff

      Hey emporilio,

      If you’re tight on space – you can certainly setup an external enclosure for the Vue 3 device (and power supply for Flexible Sensors) and then run the wire-harness/sensor wires through some conduit. Works great for a lot of customers w/ cramped panel spacing, only caveat is that you’ll want to make sure your enclosure is watertight and weatherproof.

      If deciding to skip the mains completely, totally fine as well. You won’t get your Net/Total measured but the “Total” displayed within the app will be the sum of your connected 50A CT measurements. In that way, if you’re able to capture everything w/ a 50A CT then your total there should be pretty much as accurate as if you were measuring directly w/ the 200A CT’s.

      ~Kevin