Can Vue be connected to a 15 & 20 amp breaker?

Emporia Energy Community Support Center Hardware and Installation Can Vue be connected to a 15 & 20 amp breaker?

Viewing 1 reply thread
  • Author
    Posts
    • #7011 Report Abuse
      Alphabataz
      Member

      The instructions at step 7B states wiring the Vue into two stacked 15 amp breakers. My panel is a small 100A service and there are only two normal breakers left to wire this to which are a 15A and 20A breaker. The 15 runs the furnace while the 20 runs a single outlet for the washer if it matters. If it can be wired to 20A breakers I have a double pole breaker it could connect to. They are for the kitchen outlets that share a neutral.

      Second question; is it safe to wire the white and blue harness wires under the same terminal on the neutral buss bar?

      • This topic was modified 3 years, 9 months ago by Alphabataz.
    • #7027 Report Abuse
      Emporia Support
      Emporia Staff

      Hello @Alphabataz,

      Yes, you can use a 20A breaker to tap into for powering the Vue.   Please note that the wire for the tap we supplied is only rated for 15A, so please make sure you have the right gauge wire for the larger amperage of those breakers.

      It is safe to have the white and blue from the wire harness under the terminal in the neutral bus bar.

      Please let us know if you have any further.

      Adam