Can Emporia’s EVSE Terminal take 4AWG?

Emporia Energy Community Support Center Hardware and Installation Can Emporia’s EVSE Terminal take 4AWG?

Viewing 2 reply threads
  • Author
    Posts
    • #9811 Report Abuse
      solarity
      Member

      We are looking at installing an Emporia EVSE and I am thinking of using 4/3 NM-B as 6/3 NM-B is only rated to 55A, which is below the 60A requirement for 48A. I  have run into issues before with different size conductors and terminals in thepast. Are the terminals on the Emporia EVSE big enough to take a 4AWG wire?

      Please note I am runing a neutral for potential future proof.

    • #9812 Report Abuse
      scrambler
      Member

      You can find the specs on the web site.

      They also have a large version of the 50Amp clamps

       

      Accessories

      • This reply was modified 1 year, 2 months ago by scrambler.
    • #9848 Report Abuse
      emporiacs
      Emporia Staff

      To hardwire the Emporia EV Charger you don’t need a neutral, you need 2 lives and a ground. The neutral can be connected, no problem, but ground is essential! You need to use 6 gauge for hardwire, 4 gauge will not fit in the terminals.

      Please follow the install guide and use only #6 AWG copper, 90 degrees C

Viewing 2 reply threads
  • You must be logged in to reply to this topic.