first time setup, how to adjust multiplier in France, feedback from FR welcome :

Emporia Energy Community Support Center Hardware and Installation first time setup, how to adjust multiplier in France, feedback from FR welcome :

Viewing 1 reply thread
  • Author
    Posts
    • #9334 Report Abuse
      HB38
      Member

      Hi,

       

      looking for FR guys who had already setup there GEN 2
      which value have you setup fpr multiplier ?
      using solar panel, have you only setup multiplier on mains ? or also in solar circuit as well ?

      my solar application tell me value 20% higher than GEN 2 , I will probably change on  multiplier for solar circuit by 1.2
      but what about the others ???
      my mains are managed by LINKY and it indicate also live value, do I trust that and change the multiplier for mains in the same way ?

      what about all circuits consuming power, do I need to setup 1.2 everywhere ?

    • #9338 Report Abuse
      scrambler
      Member

      You should not need a multiplier if you have a CTs on each wire.

      Are the values detected by the Gen2 CTs on your Main phases different that the values reported by the Linky?

      For solar, make sure of where your solar system is measuring.
      Most solar system with a string inverter measures the Solar panels production, which is DC power, and before inverter.
      The Gen2 will measure AC power coming out of the inverter and into the house panel, and that can be almost 10% less power than the Panel DC power.