mnradMember
Hello,
I have my Vue setup on my 240V mains (120V per phase). I am confused whether I should set the multiplier to 1 or 2 for an an accurate reading of my mains. I assume the vue senses if a load is one one CT (phase) or the other and calculates accordingly? -
Marty @EmporiaEmporia Staff
Hello @mnrad,
There is no need to put a multiplier in for your main sensors. This feature was added so customers could adjust their voltage assumption to something other than 120v per phase.
Please let us know if you have any further questions.
-
jorgito1979Member
What about when setting up the circuits and its a 240 stove what does the multiplier have to
-
kk07Member
Yes, if you have a dual pole circuit, you put one 50A sensor on one of the legs and then set multiplier to 2 in the app to correctly measure the watts used by the stove.
-
BmedflyMember
One thing I have learned over the years it was is simple to me can be hard for others to understand. I have a EE degree so these multiplier calculations seem simple. I also have many more things that are hard for me to understand than are simple. I think a web calculator where the circuit voltage is entered and the multiplier is provided would be helpful.
Technology frightens me to death. It’s designed by engineers for other engineers. And they always come with instruction booklets that are written by engineers for other engineers – which is why almost no technology ever works.
– John Cleese
-
jcuevaMember
Can you give an example of the multiplier function.
If my legs measures 137vac .
Do I devide 137/120= 1.14
-
Marty @EmporiaEmporia Staff
Hi @jcueva You are correct the multiplier if yu voltage is 137vac, would be 1.14.
-
HappyAndrewMember
So what if the voltage going to the Gen 2 was 220, but the 200 amp CV was sat on a 240 supply, can I use the multiplier to correct the calculation ? What exactly is the formula?
-
JackInTNMember
In this situation, your multiplier is 2.0, since your nominal single side of each circuit voltage is 110, so the nominal voltage across the two different phases is 220v. I hope this helps a little.
-
riekeltkeuterMember
Hi.
I have a similar question. I live in Holland, Europe. We have a 3 phase system here. Between 2 phases the voltage is ca. 400V.
So voltage between phase and null is ca. 240V. In the (dutch) manual, the instruction told me to set the multiplier to 0.25.
Unfortunately my simple meter won’t go higher as 250V, so I can’t measure the exact voltage between phases right now.
But reading the above, I think multiplier would be 120/400 = 0.3. But at the moment, I see difference in measurements between Emporia and the Smart Meter itself. The Smart meter cycles throught it’s values, and the 4th is the current live value. For example, the smart meter shows I’m using 2250 Watts, and Emporia shows 1750 Watts.
My whole point was to measure if the smart meter is correct, because I suspect it’s not, it’s 25% too high. But if the multiplier isn’t stable, I can’t tell for sure now. Maybe someone can help determing the correct multiplier factor.
If it’s true that the smart meter isn’t correct, it would cost 542 euro’s to have it tested, and after that maybe claim back to the provider.
Greetings.
-
-