Multiplier not applied in Amps

Emporia Energy Community Support Center Report a Bug Multiplier not applied in Amps

Viewing 4 reply threads
  • Author
    Posts
    • #7491 Report Abuse
      esauser
      Member

      When viewing in Amps the multiplier is not applied.

    • #7494 Report Abuse
      djwakelee
      Member

      Believe this is correct operation at this time, and a fix to an existing bug where Amps were being multiplied.  With the latest app it appears that the multiplier currently applies to volts on the circuit.  There isn’t a separate multiplier field for volts and amps, so they picked one (useful for using 1 clamp on 240V circuits).  In that case, as volts are doubled, power is also doubled appropriately.  This provides a valid workaround until proper app support for single clamp 240V is rolled out, as well as dual clamp combined summing.

      Multipliers for amps would be useful to calibrate the CT’s, or if using the Vue with alternate CT’s with different ratio.  Probably not a supported scenario.

      Believe older app versions behaved differently, where amps/volts/watts were all multiplied.

    • #7495 Report Abuse
      esauser
      Member

      What you described is what I’m doing. I have 2 240v that I’m monitoring 1 leg on, with a multiplier of 2. When looking at any other unit of measure other than amps it is properly doubled. Amps, however, are unchanged.

       

      It seems a bit odd that would be intentional since the numbers no longer line up with the totals from the mains.

    • #7496 Report Abuse
      djwakelee
      Member

      Amps shouldn’t be doubled in that case for that circuit (with the single clamp for 240V on the one leg).  The current flowing through the 240V circuit is the same whether you have 1 clamps, 2 clamps, or x clamps – on any of the legs.  What is different about using 1 clamp on 1 leg is that the voltage is 240V, versus 120V for any of the normal split phase circuits.

      What they really need to do is allow you to indicate which ports are being used for 240V circuit measurement, and the type (single or dual leg clamp).  If setup for single leg, amps is amps, and power is obtained by multiplying the measured amps by the phase 1 voltage + phase 2 voltage.  If using two clamps (such as an unbalanced subpanel feed), allow the visual list to sum up the total power.  Better support for 240V circuits has been promised in a future app update.

      So I think it is correct to not apply the multiplier to the amps (current).  Do they have an issue with the amps total and balance, that is likely.

    • #7983 Report Abuse
      bedpan
      Member

      Just discovered this bug myself. Appears to still be an issue! They need to let you specify it as a 240V Circuit. Come on guys this was reported 6 months ago I should not be re-discovering it now it should be fixed!

      Also it seems that Notifications do not work on multipliers. This is what I came to report. I will create a separate thread.