Reverse engineer a replacement heat pump size based on KW and degree days

Emporia Energy Community Energy and Technology Reverse engineer a replacement heat pump size based on KW and degree days

Viewing 3 reply threads
  • Author
    Posts
    • #8835 Report Abuse
      patman
      Member

      Our house was built 8 years ago and I’m planning on replacing my resistance boiler with an air-to-water heat pump. Like most homes, our heating system was designed with a heat loss estimate.  I started thinking that I should be able to combine the data stored by the emporia app with heat loss data for my area to extrapolate what I would need for a replacement boiler more accurately than the estimate before our house was even built.  Would that work? I’m not sure how I would even calculate it. Any ideas?

    • #8849 Report Abuse
      fclauson
      Member

      Can I suggest you do a Passive House Calculation – look at saving energy before replacing a heating unit

      https://passivehouse-international.org/index.php?page_id=266

    • #8854 Report Abuse
      Peter
      Member

      I have a 1957 built home with gas hydronic heat in the slab and second floor ceiling. I was able to get a heat loss figure in therms/degree day by using 24 months of utility bills.

    • #9394 Report Abuse
      JimiH
      Member

      I find your idea interesting.

      That being said, I’m a HVAC contractor that has been doing Manual J and Manual M load calculations for over 40 years.

      The big issue with contractors doing load calculations and then installing a system is they ALWAYS install more than is needed to cover their (you know what)

      That being said I would start with a new Manual J load calculation and then maybe extrapolate your actual heating system usage based on degree days and compare the 2.

      I have had customers use this to find out the load on their own homes. It seems pretty accurate.

      https://www.coolcalc.com/