  • in reply to: 240V (double-wide breaker) installation? #5921 Report Abuse
    cumanzor
    Member

    Marty, that’s fantastic news! Thanks!

    in reply to: 240V (double-wide breaker) installation? #5918 Report Abuse
    cumanzor
    Member

    Hi Jim! I’ve been wondering about this since I installed the Emporia in my house. So basically I ended up connecting TWO sensors to each pole of my 240v circuit as that was what the instructions implied. Then I saw the option to set a 2x multiplier in the app but really didn’t know what that meant.

    So you are saying I can connect only one sensor to one pole of a 240v circuit and then set the multiplier to 2x and that should work? (The good thing about this is that it would free up sensors for other circuits).

    Thanks!

    Carlos