January 9, 2024 at 4:44 pm in reply to: Ev Chargers with load management read power from 480VAC 3phase 3wire Delta panel #10248 Report AbusemaglitoMember
Also! Our charger ONLY supports 208 / 240VAC @ 50 / 60Hz.
Right, if I wasn’t clear: the plan is to install a large transformer between the 480VAC 3 phase delta panel and the 240VAC 3 phase subpanel where the chargers would connect.
Details here: https://drive.google.com/file/d/1VLjnDZLxE1yLJCqiHKGUdVRJwA3Pja2-/view
Contacting support basically said monitoring 480V 3 phase panels may be considered someday.
In my opinion, your devices either need a way to accept RS485 Modbus input or your datacenter could accept Modbus TCP messages from smart meters over the internet, the aforementioned Eastron meter supports this: https://www.eastrongroup.com/product/panel-board/ethernet-modbus-tcp-three-phase-panel-mounted-panel-meter-for-panel-board.html
The source IP will be unique to each customer, and you could support Dynu or ClouDNS for customer IP lookup for those customer unable to secure a static public IPv4 address. This would be the easiest way to add support for monitoring higher voltage 3 phase panels that are popular in the MDU space.
Condominiums / apartment buildings / MDUs are the big unmet need in the EV charging space. Please consider supporting this use case, as the unmet need/market potential is very large. I am happy to work with you to develop such a solution as I currently have one of these Eastron X96 meters on my network and can send Modbus TCP packets your way now.
December 16, 2023 at 4:30 pm in reply to: Ev Chargers with load management read power from 480VAC 3phase 3wire Delta panel #10164 Report AbusemaglitoMemberPerhaps this 3 phase power meter that seems to support 480V L-L and outputs to zigbee could be used?
https://www.aliexpress.us/item/3256805589951303.html?gatewayAdapt=glo2usa4itemAdapt
To communicate with the vue utility connect to enable dynamic load balance?
https://www.emporiaenergy.com/how-the-vue-utility-connect-works
Please let me know.
Anthony
December 14, 2023 at 9:37 pm in reply to: Ev Chargers with load management read power from 480VAC 3phase 3wire Delta panel #10158 Report AbusemaglitoMemberBTW, I made a similar post on reddit seeking a solution and with more details on my use case. If we can find a solution, I’ll update that post as well.
https://www.reddit.com/r/ocpp/comments/18ij0w7/has_any_heard_of_versinetic_linkray_passive/
-