  • in reply to: Multiple VUE2 Same Panel #6708 Report Abuse
    technoviolet
    Member

    For reference, this is what it looks like in my app presently with no mains registering on PNL.A.2

    in reply to: Multiple VUE2 Same Panel #6707 Report Abuse
    technoviolet
    Member

    The issue I see  with running 0.5 on the mains would be that I would be halving the actual load of only A-side or B-side 120v loads. For 2-phase circuits which are balanced, that would hold true as they are 50/50 already.

    in reply to: Multiple VUE2 Same Panel #6705 Report Abuse
    technoviolet
    Member

    @ryanhoelzer

    That certainly could work, but I’d have to rewire my branch CT(s), If I ran each VUE2 with only “A” input on one of the phases, I could use every-other breaker. I would just have to make sure on my 2-pole that I select which HOT appropriately to do the proper 2x calc. Given that the 220/240v circuits are a balanced load, that *should* work out from a math perspective.

    This seems like a rather painful setup, and this is something that could easily be solved through software 🙂

     