No kWh Reading on Used Circuits

Emporia Energy Community Support Center Hardware and Installation No kWh Reading on Used Circuits

Viewing 1 reply thread
  • Author
    Posts
    • #8277 Report Abuse
      Lizzzard817
      Member

      I just installed my Vue 2 tonight. I am getting readings on several of my circuits but not all of them. There are a few circuits I know are being used which are showing 0% and a circuit that I know is not being used showing fluctuations between 0 and  .5 kW.

      I have tandem breakers for some circuits. I put clamps on each wire individually but they are very close together. Could that be causing the issue?

    • #8282 Report Abuse
      dbeam16
      Member

      I have had this problem several times and every time but one (I am currently running 5 vue 2s) it has been because the sensor was loose in the vue 2, some times it wasn’t obvious but when pushed harder it went in a little more. The one time it wasn’t it was a bad sensor and it worked intermittently causing some frustration but emporia was great about getting me another one out.