Question about heat pump circuit on my account

Emporia Energy Community Support Center Emporia App Question about heat pump circuit on my account

Viewing 1 reply thread
  • Author
    Posts
    • #8882 Report Abuse
      JoelJoel
      Member

      Monitor seems to be working but I do see that my upstairs heat pump running in AC mode rarely/never exceeds around 300W which I think is unlikely.   Unit is on a 60A breaker multiplied 2x in the app.  Is it measuring accurately?   How can I determine if it is?

    • #8900 Report Abuse
      Emporia Support
      Emporia Staff

      @JoelJoel when using the multiplier can over/understate the circuit usage since some dual-pole circuits are not symmetrical (balanced) in their load.   To validate this you can always put two sensors on each leg for a period of time and compare their usage.  Then adjust the multiplier accordingly if you wish or just leave the sensors on each leg with no multiple.

       