  • in reply to: Spa circuit not reporting #9147 Report Abuse
    scrambler
    Member

    If you get no report from a sensor even after unplugging and plugging it back, the first thing to do is to determine if it is the port that is dead or the sensor.

    For that, swap a working sensor with the Non-working one, then check if the problem follows the sensor or stays with the port. And I mean actually unclamp a working sensor from its circuit and clamp it on the circuit of the bad sensor, and vice versa. The Circuits must stay connected to the same port on the Vue, just the sensor being used need to be swapped.

    The Vue calibration references the port, not the sensor, so no issue swapping sensors around, as long as the circuit being connected to the port does not change

    If the problem follows the sensor, then the sensor is bad (I had one died on me once), if the problem stays with the port, then there may be a problem with the port of the Vue…

     

    • This reply was modified 1 year, 5 months ago by scrambler.
    in reply to: CTs – problems with using in UK consumer Unit #9146 Report Abuse
    scrambler
    Member

    Without the detailed specifications of the Emporia sensor, it is impossible to tell.

    Have you asked them to provide the detailed specs of their sensor?

    in reply to: Solar inverter power consumption #9145 Report Abuse
    scrambler
    Member

    Can Emporia please give us an Honest answer on this.

    From the very beginning we were told the CT used on the solar input are bidirectional, and that eventually the Software would be able to read the sign and report it correctly.

    It has been years and still no change on this issue which is a major drawback for solar users.


    @emporia
    , have you given up on this feature, or is there a real short-term chance it will be done?

    Just tell us the truth 🙂

    Appreciated, and thank you for such an otherwise great product!

    scrambler
    Member

    I agree, Smart breakers is the way to go and would allow us to create a truly smart Electrical panel.

    Ideally Smart breakers should not just report (Volts, Amps & power factor), but should also be actionable remotely, so you could turn them ON or OFF remotely.  This would also open the door to the creation of scenarios like turning breakers ON or OFF automatically in a critical loads panel during an outage.

    I hope it is at the top of the list  🙂

    in reply to: Export raw data “In from grid” #9142 Report Abuse
    scrambler
    Member

    The CTs on the main leads are bi directional, so in the data file, energy exported to the grid is negative, and energy imported from the grid is positive.

    Using a tool like excel, you can separate the positive values from the negative values.

    The Total Energy Imported from the grid is the sum of all the positive values

    The Total Energy Exported to the grid is the sum of all the negative values

     

    • This reply was modified 1 year, 5 months ago by scrambler.
    scrambler
    Member

    Can this Amazon unit record overtime, and if so at what interval, for how long, and how do you download the data?

    in reply to: Correct Configuration for Multiple Vue + Solar #8595 Report Abuse
    scrambler
    Member

    You would first need to know how the two panels are interconnected, to know if you would need to just add CTS on the solar lines, or also move the 200A CTs .

    I am also not sure how long you can extend the CT wires, you should ask Emporia that question.

    If you can use a 50ft extension you could always install CTs on the Solar lines, making sure to orient them opposite as the Load CTs. But the question above needs clarification to see if you can still get a proper Net metering reading or not

    If you cant extend that far, then you would need a separate Vue, and monitor the solar separately from the rest

    scrambler
    Member

    I believe the 200A CTs are what is shown in the App as the Net production

    in reply to: Solar production monitoring #8466 Report Abuse
    scrambler
    Member

    The CTs around the solar wires are supposed to be in the reversed direction from the CTs on the drawing circuits.

    The reason they want the solar off and some loads activated suing setup, it to clearly identify the two phases on all the load wires CTs, without the solar sending power in and confusing things.

    in reply to: Will the 50A Sensor support 60A current ? #8465 Report Abuse
    scrambler
    Member

    I think I read that it is good for up to 67Amp

    in reply to: Monitoring a chain of subpanels #8235 Report Abuse
    scrambler
    Member

    If you were monitoring the sub panel with CTs on the lines going to it, but now will actually install CTS on everything inside that sub panel to monitor all the lines in it, then you should remove the CTs on the lines feeding the Sub panel, or you would be reporting the consumption twice.

    There is also no need to keep them there, as you are getting the Sub panel consumption with the sum of all its loads.

    • This reply was modified 2 years, 3 months ago by scrambler.
    in reply to: Inaccurate mains reading. #8121 Report Abuse
    scrambler
    Member

    Is your AC on a dual pole breaker, if so, do you have a CT on each of the Two poles, or are you only monitoring one of the two pole and them multiplying?

    If the pate, then the reading will most likely be wrong as I believe the AC may have an unbalanced load on both poles

    scrambler
    Member

    @natbesh, may be time to dig deeper on this …

    scrambler
    Member

    Confused …

    scrambler
    Member

    That is disappointing to hear then